Originally posted by llib:
Not much tech info in your posts, but it sounds like you left the UPS in inverter mode (or "on line", whatever...) when you enabled the external wrap-around. Big no-no. UPS always goes to internal bypass before enabling external wrap.
Originally posted by llib:
Hmmm... Two possibilities come to mind. First is that your bypass source isn't from the same source as your main input source. Our bypass source was from another transformer/switchboard, which caused us no end of misery. Maybe there's a phase difference between sources. Second possibility is a swapped phase or phase rotation error between the UPS input and the external wrap source. Wiring should be color coded: phase A is black or brown (depending on 208v or 480v), B is red or orange, C is blue or yellow.
If the vendor installed the UPS and the bypass, he should man-up and be on the hook for some of your misery... ----
And yes, you should tell your boss (who is thinking his IT hardware is protected)...